acox 3/9/19 5:46 PM

Double-tapped Square D
 
2 Attachment(s)
I wanted to double-check myself- Found a double-tapped 15-amp breaker in a Sq D panel... it's hard to get everything in 1 image, but from the label, this Type QO breaker is not rated for 2 conductors, right? Thanks!

Robert Meier 3/9/19 5:51 PM

Re: Double-tapped Square D
 
Yes QO is fine with those two conductors.

lkage 3/9/19 7:55 PM

Re: Double-tapped Square D
 
2 Attachment(s)
Attachment 205805....

cevans 3/9/19 8:46 PM

Re: Double-tapped Square D
 
Looking at the terminal, I would say rated for two. Looking at the label it shows a single...

lkage 3/10/19 8:42 AM

Re: Double-tapped Square D
 
Quote:

Originally Posted by cevans (Post 2076702)
Looking at the terminal, I would say rated for two. Looking at the label it shows a single...

Thanks, I didn't notice that.

I'll change pictures.

acox 3/10/19 12:51 PM

Re: Double-tapped Square D
 
Quote:

Originally Posted by cevans (Post 2076702)
Looking at the terminal, I would say rated for two. Looking at the label it shows a single...

Exactly why I was questioning... could it be mislabeled?

rlewis5 3/10/19 1:13 PM

Re: Double-tapped Square D
 
1 Attachment(s)
Robert is correct.

Read page 7...
https://download.schneider-electric....Ref=0730CT9801
Or just look at the attached chart from SD.

acox 3/10/19 2:10 PM

Re: Double-tapped Square D
 
I understand all that - the breaker actually has what looks like the double connector (although I can't get a good image of it), now I guess I'm just hung up on the label. The label shows it is rated for one wire, not two...

This panel was installed in 2005. Was the label different at that time?

Robert Meier 3/10/19 3:12 PM

Re: Double-tapped Square D
 
Quote:

Originally Posted by acox (Post 2076905)
I understand all that - the breaker actually has what looks like the double connector (although I can't get a good image of it), now I guess I'm just hung up on the label. The label shows it is rated for one wire, not two...

This panel was installed in 2005. Was the label different at that time?


What label, the one in the photo? That doesn't apply to the number or type of conductors. If you follow that then you cannot use stranded conductors either. The side of the CB also shows the conductor combinations. Look here at the 360 view and you can see the side of the CB.


Access Denied

mcyr 3/10/19 3:49 PM

Re: Double-tapped Square D
 
2 Attachment(s)
This is what's on the side.
Attachment 205813

Isn't this showing the same information?
Attachment 205814


acox 3/10/19 3:56 PM

Re: Double-tapped Square D
 
1 Attachment(s)
Obviously, I can't pull the breaker to look at the side, but no - the label does not show the 2 conductors shown in your 2nd image, Marcel. It shows only 1.

mcyr 3/10/19 4:16 PM

Re: Double-tapped Square D
 
Quote:

Originally Posted by acox (Post 2076965)
Obviously, I can't pull the breaker to look at the side, but no - the label does not show the 2 conductors shown in your 2nd image, Marcel. It shows only 1.

I know, I posted that to get an answer from Robert. The label on the picture I posted shows that it is allowed for double lugging, and the side view of Robert's breaker is only showing one. So I am not sure what he is indicating other than the fact if there is no label, it shows you on the side of the breaker.




acox 3/10/19 4:23 PM

Re: Double-tapped Square D
 
I guess my confusion is - do I believe the double lug that is there, or do I believe the label? I think it's obvious the double lug allows for 2 conductors, but that label... ??? If I call it out, this is the only real issue for this house, for a 1st time buyer... a kid moving out of his parents' house for the 1st time! And some electrician comes along and throws me under the bus for calling it out!?

Or I don't and this 15-amp circuit gets hot because of it...

mcyr 3/10/19 4:34 PM

Re: Double-tapped Square D
 
My opinion looking at your picture is that that particular breaker is only good for one conductor. But I am not an electrician.
If there were any other non-compliant issues in the inspection, pertaining to electrical, I would just recommend a qualified electrical contractor to evaluate and repair any issues. That being one of them.

The blade under the screw just doesn't look like it is made for two conductors.

ccurrins 3/10/19 4:41 PM

Re: Double-tapped Square D
 
Quote:

Originally Posted by acox (Post 2076977)
I guess my confusion is - do I believe the double lug that is there, or do I believe the label? I think it's obvious the double lug allows for 2 conductors, but that label... ??? If I call it out, this is the only real issue for this house, for a 1st time buyer... a kid moving out of his parents' house for the 1st time! And some electrician comes along and throws me under the bus for calling it out!?

Or I don't and this 15-amp circuit gets hot because of it...

That type of Square D breaker allows two conductors. I've installed a few panels like that and have inspected hundreds. Move on.