InterNACHI Inspection Forum
InterNACHI Inspection Forum (https://www.nachi.org/forum/)
-   Electrical Inspections (https://www.nachi.org/forum/f19/)
-   -   Service drop clearance for swimming pools? (https://www.nachi.org/forum/f19/service-drop-clearance-swimming-pools-50864/)
ktarasenko 5/14/10 4:01 PM
Howdy, Electrical Experts!
As we get ready to roll the presses on the second printing of our residential electrical inspection book (thanks to Paul Abernathy and the late, great Gerry Beaumont, may he RIP), it's come to our attention that we have a discrepancy regarding the minimum height clearance for swimming pools.
Can someone advise, please (without relying on the online residential electrical course, since we will likely need to make a correction there, too)? I believe our source should be the NEC, but Nick asked me to throw the question out to you guys.
Thanks to member Ron [StillTryingtoFindOutHisLastName] for catching this! ;)
Robert Meier 5/14/10 4:14 PM
Re: Service drop clearance for swimming pools?
This is from a previous thread. I had to paste it together since the Table could not be copied as it appears in the NEC. For more complete information check out Table 680.8:
Quote:
680.8 Overhead Conductor Clearances.
Overhead conductors shall meet the clearance requirements in this section. Where a minimum clearance from the water level is given, the measurement shall be taken from the maximum water level of the specified body of water.
(A) Power. With respect to service drop conductors and open overhead wiring, swimming pool and similar installations shall comply with the minimum clearances given in Table 680.8 and illustrated in Figure 680.8.
FPN: Open overhead wiring as used in this article typically refers to conductor(s) not in an enclosed raceway.
Table 680.8 Overhead Conductor Clearances
Insulated Cables, 0750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor:
Clearance Parameters:
A. Clearance in any direction to the water level, [6.9m or 22.5 feet]
edge of water surface, base of diving platform, or
permanently anchored raft
ccurrins 5/14/10 4:14 PM
Not quite what you're looking for, but this is what our utility company says about pool clearance.
AMEREN ELECTRIC SERVICEMANUAL 800−2 06/25/09
Clearances of Services over Swimming Areas
Although it is possible to have services over swimming areas, this practice is discouraged. It is necessary that the maximum conductor sag under various operating and environmental conditions be determined. Contact your local Ameren representative for assistance.
ktarasenko 5/14/10 4:34 PM
That's what we have in a chart in the course (22'6"). The discrepancy is in a graphic that was created by one of our former graphics folks, but the measurement is either old or just wrong.
Thanks for taking the time to post!
If we have any more thumbs-ups or thumbs-downs on this, please keep posting!
(And I couldn't agree more with CCurrins -- the idea of being in an outdoor pool situated beneath a service drop would have me shaking...!)
gbell 5/14/10 5:13 PM
This is what we follow in florida.
424.1.4.2.4 Overhead wiring. Overhead service wiring shall not pass within an area extending a distance of 10 feet (3048 mm) horizontally away from the inside edge of the pool walls, diving structures, observation stands, towers or platforms. Allowances for overhead conductor clearances to pools that meet the safety standards in the National Electrical Code may be used instead.
Robert Meier 5/14/10 5:17 PM
Can you post the graphic?
ktarasenko 5/14/10 5:37 PM
1 Attachment(s)
Quote:
Please see attached. (Nick told me not to do this initially.)
The "10 feet away" is not in dispute; it's the height between the service drop and the pool.
Robert Meier 5/14/10 5:41 PM
According to the NEC it should be 22.5' above the water level.
ktarasenko 5/14/10 5:59 PM
OK, Guys --
Thanks for weighing in. I'm going to correct the measurement in the graphic, and Nick will upload the replacement to the Image Library as soon as he gets it from me.
Be sure to download it for yourselves if you have our CD of images.
Have a great weekend!
pabernathy 5/15/10 9:58 AM
Lol...so much for being an author of anything....lol.....typical
Copyright © International Association of Certified Home Inspectors